CHAPTER 2 DEPENDENCE FUNCTIONS
>SET SEQUENCE/EVENT 1,1,J=2
>SET SEQUENCE/EVENT 2,4,J=1
>SET SEQUENCE/EVENT 2,2,J=3
>SET SEQUENCE/EVENT 3,4,J=1
>SET SEQUENCE/EVENT 3,2,J=0
>SET SEQUENCE/LATCH 1,1,2
>SET SEQUENCE/LATCH 2,3,0
>SHOW SEQUENCE
Sequencer Enable
level1 level2 level3 level4 level5 level6 level7 level8
1 |1|#>2 | | | | | | | | | | | | | |
2 | | |2|->3 | | | | | | | | | | | |
3 | | | | |3|#end | | | | | | | | | |
4 | | |4|->1 |4|->1 | | | | | | | | | |
5 | | | | | | | | | | | | | | | |
6 | | | | | | | | | | | | | | | |
7 | | | | | | | | | | | | | | | |
8 | | | | | | | | | | | | | | | |
T | | |T|->1 | | | | | | | | | | | |
Latch 1 (1->2) = 00m02s060ms379.0μs Latch 2 (3->E) = 00m16s040ms650.0μs
Indicates
that, if event
1 occurs at
level 1, move
to level 2 and
let the timer
latched.
Indicates that, if event 3
occurs at level 3, the
sequencer terminates and
let the timer latched.
Indicate time values of timer latch 1 and timer latch 2. The time
value, deducting the value of the timer latch 1 from the value of the
timer latch 2, represents the execution time.
Time is displayed in the following format.
00 m 00 s 000 ms 000.0 μs
minutes
seconds
milliseconds
microseconds